120 sq ft outbuilding, separate panel in building one 20A 208 tandem breaker, one 20 A for single LED ceiling lamp, 2 20 V outlets on single 20A breaker.
I installed 3 wire 10 AWG thwn in 3/4 RMC with 30A breaker of phase A-B in main panel. Everything in conduit.
Local AHJ said 6 AWG and 60A breaker required. I just said 'yes sir' rather than argue, but
Lots of existing 225.39 threads, but there is one AHJ out there that interprets as a 60A feeder needed. And of course 2 ground rods , etc...
I installed 3 wire 10 AWG thwn in 3/4 RMC with 30A breaker of phase A-B in main panel. Everything in conduit.
Local AHJ said 6 AWG and 60A breaker required. I just said 'yes sir' rather than argue, but
Lots of existing 225.39 threads, but there is one AHJ out there that interprets as a 60A feeder needed. And of course 2 ground rods , etc...