When installing a pool sub panel on the exterior of a home in Florida, are the feeders required to be 60 amp rated per 229.39(B)?
Sorry 225.39 (D) is correct. A pool is a separate structure. Conductors are run outside of the main structure to a panel sometimes mounted on the main structure. What I am trying to grasp is #12 thhn conductors run in 3/4” conduit to a 60 amp panel for a pool. Yes it works for the pump and a light, but as soon as you add the additional equipment (pool heater) everything is to small.
I appreciate your replies as it helps all of us!
225.39 (D) not less than 60 amperes
225.39 Rating of Disconnect. The feeder or branch-circuit
disconnecting means shall have a rating of not less than the
calculated load to be supplied, determined in accordance with
Parts I and II of Article 220 for branch circuits, Part III or N of
Article 220 for feeders, or Part V of Article 220 for farm loads.
Where the branch circuit or feeder disconnecting means
consists of more than one switch or circuit breaker, as permitted
by 225.33, combining the ratings of all the switches or
circuit breakers for determining the rating of the disconnecting
means shall be permitted. In no case shall the rating be
lower than specified in 225.39(A), (B), (C), or (D).
(D) All Others. For all other installations, the feeder or
branch-circuit disconnecting means shall have a rating of not
less than 60 amperes.
The pool pump is 3 wire.
Are pool heaters common in Florida?Sorry 225.39 (D) is correct. A pool is a separate structure. Conductors are run outside of the main structure to a panel sometimes mounted on the main structure. What I am trying to grasp is #12 thhn conductors run in 3/4” conduit to a 60 amp panel for a pool. Yes it works for the pump and a light, but as soon as you add the additional equipment (pool heater) everything is to small.
I appreciate your replies as it helps all of us!
225.39 (D) not less than 60 amperes
yes, very common because of pool screen cages.Are pool heaters common in Florida?
Do they provide shade?Exactly,
Required 60 amp disconnecting means in the main panel would require 60 amp rated conductors.
Or
30 amp minimum for the two-2 wire branch circuits.
So is a 20 amp breaker feeding #12 wire to a pool panel compliant?
yes, very common because of pool screen cages.
Are you asking if a pool panel feeder can be 20A?Exactly,
Required 60 amp disconnecting means in the main panel would require 60 amp rated conductors.
Or
30 amp minimum for the two-2 wire branch circuits.
So is a 20 amp breaker feeding #12 wire to a pool panel compliant?
yes, very common because of pool screen cages.
Exactly,
Required 60 amp disconnecting means in the main panel would require 60 amp rated conductors.
Or
30 amp minimum for the two-2 wire branch circuits.
So is a 20 amp breaker feeding #12 wire to a pool panel compliant?
yes, very common because of pool screen cages.
the feeder or
branch-circuit disconnecting means shall have a rating of not
less than 60 amperes.
I wrote a code change proposal to try and clarify this section because it makes no sense. Why can I run #10 or #12 wire to a separate structure, install a breaker panel and then install a 60 amp main breaker. That is what this section is allowing. When I wrote the proposal they rejected it and said that it is written exactly as they want it.
Again, if the panel is mounted to the building then there is NO code that states 60 amps or, anything else for that matter, is required. It would be the same as a panel mounted inside the structure.
If the feeder went out to a structure by the pool and mounted out there that would be different but the feeder does not have to be 60 amps.