fmtjfw
Senior Member
- Location
- Fairmont, WV, USA
Section/Paragraph: 225.52(C) Disconnecting Means. Locking. Exception
New Text
225.52 Disconnecting Means.
....
(C) Locking.
Disconnecting means shall be lockable in accordance with 110.25.
Exception: Where an individual disconnecting means consists of fused cutouts, a suitable enclosure capable of being locked and sized to contain all cutout fuse holders shall be installed at a convenient location to the fused cutouts.
Substantiation
The period to end the sentence in the exception is missing.
Inserted Deleted
New Text
225.52 Disconnecting Means.
....
(C) Locking.
Disconnecting means shall be lockable in accordance with 110.25.
Exception: Where an individual disconnecting means consists of fused cutouts, a suitable enclosure capable of being locked and sized to contain all cutout fuse holders shall be installed at a convenient location to the fused cutouts.
Substantiation
The period to end the sentence in the exception is missing.
Inserted Deleted