Section/Paragraph: 225.6(C) [new section]
Added Text
225.6 Conductor Size and Support.
(C) Power Cable Assemblies. Cable assemblies that meet utility standards for neutral-supported power cable assemblies are acceptable for use outdoors for feeders or branch circuits. The use of the uninsulated conductor shall be limited by the provision of this Code.
Informational Note: See ANSI/ICEA S-76-474 Insulated Cable Engineers Association Standard for Neutral-Supported Power Cable Assemblies with Weather-Resistant Extruded Insulation Rated 600 Volts
Substantiation:
Million of miles of cable meeting this standard are used in the United States and around the world in all climatic conditions. The failure rate of the cable (barring mechanical damage such as falling trees and large branches or felled utility poles) is miniscule. It is a proven technology.
insert delete
Added Text
225.6 Conductor Size and Support.
(C) Power Cable Assemblies. Cable assemblies that meet utility standards for neutral-supported power cable assemblies are acceptable for use outdoors for feeders or branch circuits. The use of the uninsulated conductor shall be limited by the provision of this Code.
Informational Note: See ANSI/ICEA S-76-474 Insulated Cable Engineers Association Standard for Neutral-Supported Power Cable Assemblies with Weather-Resistant Extruded Insulation Rated 600 Volts
Substantiation:
Million of miles of cable meeting this standard are used in the United States and around the world in all climatic conditions. The failure rate of the cable (barring mechanical damage such as falling trees and large branches or felled utility poles) is miniscule. It is a proven technology.
insert delete