Is it code compliant to feed a 225 amp panel from a 200 amp meter socket?
The socket is rated for 200 amp continuous duty.

Thanks
 
230.90 limits service OCPD rating to not more than service conductor ampacity. It should limit it to the lesser of conductor ampacity or equipment rating... but that's a discussion for another day.
 