N nizak Senior Member Jul 9, 2016 #1 Is it code compliant to feed a 225 amp panel from a 200 amp meter socket? The socket is rated for 200 amp continuous duty. Thanks
Is it code compliant to feed a 225 amp panel from a 200 amp meter socket? The socket is rated for 200 amp continuous duty. Thanks
D dmxtothemax Senior Member Location Brisbane, Queensland, Australia Jul 9, 2016 #2 What size is the main breaker ? is it 200A or 225 a ?
Smart $ Esteemed Member Location Ohio Jul 9, 2016 #3 230.90 limits service OCPD rating to not more than service conductor ampacity. It should limit it to the lesser of conductor ampacity or equipment rating... but that's a discussion for another day.