Is a 200 amp meter rated for 225? Or, do I need a 320/400. Also, is there a code reference to manual meter bypasses?
 
Around here we us the same meterbases for 200A and 225A. Bypasses in meterbases is a POCO thing not an NEC issue.
 
sid123456 said:
Is a 200 amp meter rated for 225? Or, do I need a 320/400. Also, is there a code reference to manual meter bypasses?

A 200 amp meter base is rated for 200 amps noncontinuous load and 160 for continuous load.

You will need a 400 amp base-- it is rated 320 for continuous load and 400 noncontinuous.
 
C3PO said:
Around here we us the same meter bases for 200A and 225A.
Don't forget that we don't follow the same rules that you have to follow. You are correct, we use a class 200 meter and a 200 ampere meter fitting for a 225 ampere service but you are not permitted to do the same. Ours come with a lifetime guarantee. :smile:
 
A 200 amp base on a 225 amp service has always concerned me, but I can't say I have ever honestly seen a resulting problem.
Here the meter base is a POCO call and to the inspectors is "invisible".
 