Are you intending to install this as an SDS (separately derived system) or not?
No SDS
Not sds
No SDS
Good question. If you are allowed to do it with an autotransformer, there should be no prohibition on doing the same thing with an isolation transformer. But it is not clear that there are any advantages to doing it that way.Is that even and option under the NEC?
Good question. If you are allowed to do it with an autotransformer, there should be no prohibition on doing the same thing with an isolation transformer. But it is not clear that there are any advantages to doing it that way.
Separately Derived System. A premises wiring system
whose power is derived from a source of electric energy or
equipment other than a service. Such systems have no direct
connection from circuit conductors of one system to
circuit conductors of another system, other than connections
through the earth, metal enclosures, metallic raceways,
or equipment grounding conductors.
I think that by NEC definition the OPs and all isolation transformers are SDS.
If the transformer itself had an X0 to H0 bond, it could not, under that definition be part of an SDS.
other than connections
through the earth, metal enclosures, metallic raceways,
or equipment grounding conductors.
To make it a non-SDS installation, of course.How and why would there be a direct bond from XO to HO?
To make it a non-SDS installation, of course.
And I will stick with why is a non-SDS generator compliant while a non-SDS transformer is not, aand yet an autotransformer is.I am sticking with not compliant.
I am sticking with not compliant.
Seems like if there was nothing wrong with this then everyone would do it to avoid the gec requirement.
What would you cite as a code violation?
Of course I have not priced a Wye / Wye trans and the neutral you would have to run to it
Exactly. It is an economic decision rather than a regulatory one.Well that's a good point.....I think I'd rather install the GEC.
Exactly. It is an economic decision rather than a regulatory one.