225kva xfmr installation

Status
Not open for further replies.

jibron

Member
Location
Ohio
I’m using a 225kva to step up 208 to 480/277 wye.
450.21 (B) is telling me I need to construct a transformer room unless I qualify for the exception calling for “Class 155 or higher insulation systems “ on my transformer. Can someone tell me what exactly that is? Here is my tag.

909C0BCF-9A67-41C8-A8EE-353DF6F0F7B4.jpeg
 
Something that the requirements don't make explicitly clear. You have a 'NEMA insulation class'. It just happens that the insulation class number is the same as the max temperature allowed in degrees C.


So when the dataplate says 'Temp Class 220°C' that implies a NEMA insulation class 220, which exceeds NEMA insulation class 155

-Jon
 