Riograndeelectric
Senior Member
- Location
- Lakewood Colorado
I am estimating to a job to run power to a new detached garage 2-20amp circuits feed over head to detached garage. the garage feeder will run across the back yard so no clearance issue here can maintain 10 foot clearance from house to detached garage
my question is the understanding of 230.24 thru 234.24 (A) exceptions 1,2 &3.the way I read 230.24 in regards to service drop conductors passing over entire roof of Detached garage and laying on the roof of the Garage . prior to Garage service drop conductors were at 13 ft above ground at the service entrance conductors.
the service drop conductors coming from the Utility Pole are now laying on the roof of the Garage so as I read 230.24 Thur 230.24 (A) exceptions 1,2 & 3 is I must maintain 8 foot clearance above the Garage roof, since the service drop conductors cross over the entire roof of the garage
am I reading 230.24 correctly?
Thanks.
Cameron
my question is the understanding of 230.24 thru 234.24 (A) exceptions 1,2 &3.the way I read 230.24 in regards to service drop conductors passing over entire roof of Detached garage and laying on the roof of the Garage . prior to Garage service drop conductors were at 13 ft above ground at the service entrance conductors.
the service drop conductors coming from the Utility Pole are now laying on the roof of the Garage so as I read 230.24 Thur 230.24 (A) exceptions 1,2 & 3 is I must maintain 8 foot clearance above the Garage roof, since the service drop conductors cross over the entire roof of the garage
am I reading 230.24 correctly?
Thanks.
Cameron