- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
In article 230.40 ex. #3, it says this:
Meaning on a single family dwelling you could have a 400A (320A) meter base with dual lugs and feed a 200A panel at the house and feed another building/structure with 200A. Each location would be service entrance conductors and neither would be a feeder. That's allowing one service drop to supply two sets of SE conductors.
The problem I'm having is the inspector is saying he's ok with the two sets of SE conductors but not ok with not grouping the disconnects. On the house the meter is back to back with the inside panel, no disconnect. At the other structure there is a main breaker panel/disconnect mounted on the outside of the structure. I'm pretty sure we have had this discussion before and I looked for the allowance. What I found, and think is the section that allows this is 230.71, which says:
The part in bold is what I think would allow the disconnecting means not to be grouped.
What are your thoughts on this?
A one-family dwelling unit and its accessory structures
shall be permitted to have one set of service-entrance conductors
run to each from a single service drop, set of overhead service conductors,
set of underground service conductors, or service lateral.
Meaning on a single family dwelling you could have a 400A (320A) meter base with dual lugs and feed a 200A panel at the house and feed another building/structure with 200A. Each location would be service entrance conductors and neither would be a feeder. That's allowing one service drop to supply two sets of SE conductors.
The problem I'm having is the inspector is saying he's ok with the two sets of SE conductors but not ok with not grouping the disconnects. On the house the meter is back to back with the inside panel, no disconnect. At the other structure there is a main breaker panel/disconnect mounted on the outside of the structure. I'm pretty sure we have had this discussion before and I looked for the allowance. What I found, and think is the section that allows this is 230.71, which says:
230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service
permitted by 230.2, or for each set of service-entrance
conductors permitted by 230.40, Exception No. 1, 3, 4, or 5,
shall consist of not more than six switches or sets of circuit
breakers, or a combination of not more than six switches and
sets of circuit breakers, mounted in a single enclosure, in a
group of separate enclosures, or in or on a switchboard or in
switchgear. There shall be not more than six sets of disconnects
per service grouped in any one location.
The part in bold is what I think would allow the disconnecting means not to be grouped.
What are your thoughts on this?