Actually, I guess this is actually a 480v service with a wild leg correct?
Yep. Ive never heard of one either but they do exist apparently. I went ahead and figured out the voltage arrangement by hand. Looks like there is 415v between the wild leg and neutral, 240v phase to neutral, 480 phase to phae.
The conventional notation would be 480/240V 3? 4W and perhaps append Open Delta where indicating transformer configuration.NO SUCH THING .
Well of course there is. The nominal is different.NO SUCH THING .
3 Services
3.1 Types of Service Furnished
Available electric service includes 60 hertz, alternating current, single-phase or three-phase. See Section 3.10, Load Requirements. The nominal secondary voltages are provided below.
Underground Service
The following underground service may be provided:
* Single-phase, 120/240-volt, three-wire, grounded
* Single-phase, 240/480-volt, three-wire, grounded
* Single-phase, 120/208-volt, three-wire, grounded
* Three-phase, 208Y/120-volt, four-wire, grounded, wye
* Three-phase, 480Y/277-volt, four-wire, grounded, wye
* Three-phase, 240/120-volt, four-wire, grounded, open-delta1
* Three-phase, 480/240-volt, four-wire, grounded, open-delta1
Overhead Service
The following overhead service may be provided:
* Single-phase, 120/240-volt, three-wire, grounded
* Single-phase, 240/480-volt, three-wire, grounded
* Three-phase, 208Y/120-volt, four-wire, grounded, wye
* Three-phase, 240/120-volt, four-wire, grounded, delta
* Three-phase, 480Y/277-volt, four-wire, grounded, wye
* Three-phase, 480/240-volt, four-wire, grounded, open-delta (motor loads are limited to 40 hp or less unless equipped with ASD)
If other service voltages are required - such as three-phase, 480/240-volt, grounded, delta - the Customer must request and PGE must approve these voltages before services can be provided.
Yes. Very irritating. Also a lot of old posts have lost things like degree symbols.PS: Is anyone else having problems with editing their post.
Also your post disappears after a preview. What a pain!!!:rant:In IE and Chrome I edit my post and click Save Changes. The litter spinner shows, but nothing else happens.
Ditto for that and other symbols. I hate it.:rant:I've been having to click Go Advanced to save changes. Currently I'm attempting to change the ? after 3 to the phase character. I was pretty sure I put in the proper character on initial post... but now no matter what I try I can't change it to "?" in Chrome...
NO SUCH THING .
The bigger question is, do you NEED some small amount of 240V single phase for something? Keep in mind, this will NOT be 120/240V single phase, it is ONLY 240V from phase to neutral. That means your 240V load will not be connected line-to-line, but line-to-grounded neutral, and if anything else inside of it is assuming line to neutral will be 120V, it will fry.
In my opinion its going to be oddball enough to cause some future electrician, i.e. one who believes it doesn't exist, to make some sort of disastrous mistake.
Also, I have one 240v-3 phase load, and I had a hard time wrapping my head around that this couldnt be serviced with a phase to phase connection. I wonder if this could be connected with the neutral and a phase?
Either you are saying something incorrectly here, or you should leave this to professionals. Phase to neutral would be SINGLE phase, not 3phase.
I meant 240-1. Sorry for the confusion in your presence.
Ok, didn't mean to offend, but realize that this is a site FOR electricians, not to be used IN LIEU of electricians.
I know what you mean. In my experience, when someone starts a remark off with something like "I don't mean to sound racist..." it's usually followed something extremely racist.I find that when people say "I didnt mean to be _______....", that they actually did mean to be what ever goes in the blank.