230.54 (E) Separately bushed openings- does this matter for single phase residential services?

Status
Not open for further replies.

Brendon Smith

Member
Location
Middleton ID
Occupation
Building Inspector
230.54 (E) Separately bushed openings- does this matter for single phase residential services? I’m new and trying to figure this out.. Do single phase services have conductors of different potential?
Or is this just for 3 phase services?


Sent from my iPhone using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It applies to 1ph and 3ph.

Only paralleled wires of the same phase would not have different potential between them.

The intent is to have insulating material between the wires in addition to that on the wires.

Any standard weatherhead has a plastic insert that accomplishes what they're referring to.