Electrick One
Member
- Location
- North Carolina
I'm going round and round with a local inspector about an application.
On a commercial application,I have proposed to run service entrance conductors,in parallel, from a meter base, thirty feet, along an outside wall, at a height of nine feet, entering the building, and terminating into a 600 amp MDP with a main, within five feet of entering the structure. Are the conductors still considered outside the building, or will overcurrent protection need to be provided at the meter location? The inspector thinks the later should apply. There is no mention of this condition in 230-6, however I have used this application in the past,without problem. Are there any exceptions that cover this application?
On a commercial application,I have proposed to run service entrance conductors,in parallel, from a meter base, thirty feet, along an outside wall, at a height of nine feet, entering the building, and terminating into a 600 amp MDP with a main, within five feet of entering the structure. Are the conductors still considered outside the building, or will overcurrent protection need to be provided at the meter location? The inspector thinks the later should apply. There is no mention of this condition in 230-6, however I have used this application in the past,without problem. Are there any exceptions that cover this application?