My 2008's in the truck, and it's raining, so hopefully the '05 is the same, give or take...
1.) NEC Section/Paragraph: 230.70(A)(1)
2.) Proposal/Comment Recommends: [deleted text]
3.) Proposal/Comment: (1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
(Red text deleted)
4.) Substantiation: Allowing service equipment indoors poses an unnecessary risk to personnel and property, usually for asthetic reasons. Services supplied by raceway wiring methods provide pathways into a structure for both arc blast events contained in the laterals themselves as well as outdoor tranformer explosions.
Attached are two events that occurred within a month of each other, within 20 miles of each other. In both events, there were personnel present who could have been seriously injured by the explosions and subsequent fires from service lateral and outdoor transformer faults.
Source: Bank Fire, Fort Collins, CO
Source: Good Samaritan Fire, Windsor, CO
There is no reason to allow deadly equipment to be installed inside a building for asthetic reasons.
(end)
This ought to spur a discussion...
1.) NEC Section/Paragraph: 230.70(A)(1)
2.) Proposal/Comment Recommends: [deleted text]
3.) Proposal/Comment: (1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
(Red text deleted)
4.) Substantiation: Allowing service equipment indoors poses an unnecessary risk to personnel and property, usually for asthetic reasons. Services supplied by raceway wiring methods provide pathways into a structure for both arc blast events contained in the laterals themselves as well as outdoor tranformer explosions.
Attached are two events that occurred within a month of each other, within 20 miles of each other. In both events, there were personnel present who could have been seriously injured by the explosions and subsequent fires from service lateral and outdoor transformer faults.
Source: Bank Fire, Fort Collins, CO
An electrical fire Monday morning at the Wells Fargo Bank located at 3500 John F. Kennedy Parkway has closed the bank for an undetermined amount of time.
The fire was caused when a concrete boring machine came in contact with a high voltage underground electric line going into the building. A utility contractor was working at the property at the time, said PFA Assistant Fire Marshal Holger Durre.
Poudre Fire Authority responded to the fire at 11:52 a.m. with five fire engines and had the flames contained within 15 minutes of arriving on the scene.
The first crews found fire coming from a transformer on the exterior of the building. Smoke had also filled the basement of the building.
There were no injuries in the fire, although PFA Assistant Fire Marshal Shawn Brann said one person was trapped in an elevator because electricity was cut to the building.
Mardene Abarbanell, a Fort Collins resident who banks with Wells Fargo, said she was in the bank when the fire started. She said there was a loud explosion that caused the building to shake and that sounded like it came from the roof.
"It was just the most frightening thing I've ever experienced," she said. "My first thought was it sounded like an airplane had hit the roof because the building shimmied."
Source: Good Samaritan Fire, Windsor, CO
In the Windsor event, there was an electrician inside the described electrical room minutes before the electrical equipment inside the room exploded, literally off the walls they were mounted to. He was reacting to the transformer accident outside, shutting down electrical equipment inside the building to isolate the premises wiring system from the utility. If he had lingered in the room he would be dead.According to fire chief Brian Martens, the first occurred around 7 a.m. Tuesday when a padmount electrical transformer at the Good Samaritan Society, Water Valley Resort, under construction, started on fire after a construction worker contacted it with a construction lift, short circuiting the transformer.
The fire was further hindered when gas built up in conduit that leads to the electrical room exploded.
Structural damage to Good Samaritan facility was contained in the electrical room with some wall damage, Martens said.
It took firefighters about 90 minutes to extinguish the fire, which was ruled accidental.
There is no reason to allow deadly equipment to be installed inside a building for asthetic reasons.
(end)