Why do you need barriers between main breakers? This change does nothing practical in my view.....
You mean separate compartments
Barriers to me means some sort of isolation, so, the question to me is, why do we need some type of isolation between main breakers?
Not sure.
Is it so if we shut off one main we have some type of isolation from another energized service disconnect that may be in close proximity?
That would be my guess.
JAP>
Yes the primary will still be hot, but, if in a compartment, the load side of a main wouldn't be close to another service breaker that is still on as it would be if in a MLO panel with breakers right next to each other.
I'm curious of the actual reasoning myself.
Just throwing my 2 cents in to see if I'm anywhere close to the actual reason.
JAP>
So you want us to be required to have a single Main Disconnect ?
If that's the case why not have them do away with the 6 movement rule all together?
JAP>
The line side insulating barriers are required on all exposed line side energized parts. The separate enclosure eliminates exposure to energized load side parts for other service disconnects if they would be in a common enclosure. With a single disconnection device in the enclosure, there are no live energized parts in the enclosure when the disconnect is open.