ShauwnC
Member
- Location
- Fairfax virginia
We have a job with a 400 amp twin service ( two 200 amp main breaker panels ).
We installed a 20kw generator with a 200amp service rated ats. The inspector rejected the job quoting article 230.72(a) grouping of disconnects. I have spoken to the inspector quoting 230.72(b). I am having difficulty understanding the wording and intent of 230.72(b) and if I am in the right here. The inspector is saying that I have to either install a disconnect on the "non emergency" panel or move the transfer switch inside. I want to know if I am covered by 230.72(b) as both panels have main breakers. Please help.
We installed a 20kw generator with a 200amp service rated ats. The inspector rejected the job quoting article 230.72(a) grouping of disconnects. I have spoken to the inspector quoting 230.72(b). I am having difficulty understanding the wording and intent of 230.72(b) and if I am in the right here. The inspector is saying that I have to either install a disconnect on the "non emergency" panel or move the transfer switch inside. I want to know if I am covered by 230.72(b) as both panels have main breakers. Please help.