It has been presented that an automatic transfer switch with service disconnect is permissible to be installed ahead of a service disconnect as per 230.82(5) as this will be fed with circuits for standby power systems. In this sceanario, the grounding electrode system and specifically the main bonding jumper will remain in the existing service disconnect. The opponents of this concept present that where an automatic transfer switch with a service disconnect is installed ahead of a service disconnect that the grounding electrode system and the main bonding jumper need to be relocated to the automatic transfer switch as this is now the service disconnect.
My opinion, is that the essence of 230.82(5) is to allow the ATS with service disconnect ahead of the existing service disconnect without relocating the grounding electrode system and the main bonding jumper. If this is not the case, then what's the point of the article? Part of the article states that this must be installed in accordance with requirements for service-entrance conductors. As such, the ATS is not the service disconnect and the grounding electrode system and the main bonding jumper remain in the existing service disconnect.
My opinion, is that the essence of 230.82(5) is to allow the ATS with service disconnect ahead of the existing service disconnect without relocating the grounding electrode system and the main bonding jumper. If this is not the case, then what's the point of the article? Part of the article states that this must be installed in accordance with requirements for service-entrance conductors. As such, the ATS is not the service disconnect and the grounding electrode system and the main bonding jumper remain in the existing service disconnect.