230.85 B1 question

Status
Not open for further replies.

mavrck

Member
Location
ky
The customer wants to install a 200 amp panel across the house from the meter base. So I will plan to install a emergency service disconnect outside with the meter. I going to install a meter socket load center with 200 amp breaker that has feed thru lugs. I have looked through the code book but couldn't find if I could use a main lug only panel in the house since my disconnect/ocpd will be outside? Or does the panel inside the house also need a main breaker. With adding the emergency service disconnect this now makes the panel inside a sub panel. Thx
 
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcur‐ rent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panel‐ board.
 
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcur‐ rent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panel‐ board
Sounds like it will work. Thx
 