Minuteman
Senior Member
- Location
- The Sooner Nation
I'm in Nashville visiting my Dad and Brother. However, before I left we failed an inspection when I updated the service to a two-story duplex home built in 1939. Each unit had only 60 amps apiece. Both services had been added to several times over the years. The lower unit had a 100-amp newer panel in the basement. The upper unit had a fused disco in the basement that fed a 100-amp panel in the utility room of the upper unit. Both also had other circuits feed from the basement
Since the general location of the feeders/branch circuits was in the basement, I decided to keep the service location in the same place and just update most everything.
I installed a 2" EMT riser from the new meter twin pack up the wall centered between the basement door and a lower window about 2 feet apart. The riser also passess a upper windows about foot away. The WH is installed about 10" above the upper window and the SE drip loop is about 4" above the window. There is a service knob on the opposite side of the riser that the window.
The AHJ uses the 2002 cycle. The inspector red tagged the install, not because of the WH/drip loop, but because the riser is passes only about 12" from the windows.
Am I reading the code wrong? Can the riser be installed close to the windows as long as the SE cables are above it?
Since the general location of the feeders/branch circuits was in the basement, I decided to keep the service location in the same place and just update most everything.
I installed a 2" EMT riser from the new meter twin pack up the wall centered between the basement door and a lower window about 2 feet apart. The riser also passess a upper windows about foot away. The WH is installed about 10" above the upper window and the SE drip loop is about 4" above the window. There is a service knob on the opposite side of the riser that the window.
The AHJ uses the 2002 cycle. The inspector red tagged the install, not because of the WH/drip loop, but because the riser is passes only about 12" from the windows.
Am I reading the code wrong? Can the riser be installed close to the windows as long as the SE cables are above it?