I'm reading those sections trying to decipher what exactly is says.
230.80 makes it sound like if you have more than one service disconnect it they must add up to the capacity of the feeder. IE: 200 amp service. 150amp breaker and a 50amp breaker.
230.90(A) Exception 3 says the sum of multiple over current devices can exceed the feeder capacity.
So one says that the disconnecting means cannot exceed the feeder capacity while the other says the overcurrent protection can. I need help here.
230.80 makes it sound like if you have more than one service disconnect it they must add up to the capacity of the feeder. IE: 200 amp service. 150amp breaker and a 50amp breaker.
230.90(A) Exception 3 says the sum of multiple over current devices can exceed the feeder capacity.
So one says that the disconnecting means cannot exceed the feeder capacity while the other says the overcurrent protection can. I need help here.