- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Can I have a service load calculated value of 2,500 amps, a set of service conductors rated for 3000 amps, a service switchboard rated for 3000 amps, and a service disconnecting means that comprises a set of 6 circuit breakers that add up to 4,225 amps?
I am reviewing a coworker's design that has this situation. I was about to throw a flag on the play, but I wanted to check the actual code language first. I saw nothing in 408 that explicitly deals with this question. There is Table 450.3(A) and its Note 2. But the utility owns the transformer, and we do not yet know what KVA rating it will have. Then I read 230.90(A), and thought I had the basis for criticizing the design. However, Exception 3 has me confused. It looks a little bit like the rule about using the next higher standard breaker rating, so long as you are under 800 amps. But this Exception does not put an 800 amp limit into play.
Can anyone clear this up?
I am reviewing a coworker's design that has this situation. I was about to throw a flag on the play, but I wanted to check the actual code language first. I saw nothing in 408 that explicitly deals with this question. There is Table 450.3(A) and its Note 2. But the utility owns the transformer, and we do not yet know what KVA rating it will have. Then I read 230.90(A), and thought I had the basis for criticizing the design. However, Exception 3 has me confused. It looks a little bit like the rule about using the next higher standard breaker rating, so long as you are under 800 amps. But this Exception does not put an 800 amp limit into play.
Can anyone clear this up?