System, 277/480VAC from the utility
If we have a single 1000AMP service coming from the utility to a single CT Cabinet mounted on the outside wall of a building.
Leave the CT cabinet and go to two 600AMP service rated main fused disconnects located on the inside wall opposite the CT cabinet. Further distribution within the building is accomplished with panelboards fed by the two 600Amp fused disconnects.
Is Ground Fault Protection required?
The way I am reading this section, GFP is not required since the two fused disconnects are less than 1000Amps.
Looking for a second/third/forth opinion.