Yep. Once, a vendor installed a motor controller (contactor switch) and routed the GF relay contacts to open the switch (contactor) if a ground occurs! The contactor switch contacts got damaged due excessive ground fault current experienced after a motor ground fault! The solution to the problem was routing the GF contact trip to the shunt trip contact of the supply breaker! The breaker has a higher interrupting rating than the contactor switch!This is my vision of situation in example.
At the point of installation we have 100kA available S.C.
800A rated switch with a trip relay controlled by ground fault controller opens the switch at current between 1,100A - 10,000A.
At 10kA and above ground fault, the controller will allow fuses to open the fault.