The load need not have a neutral, but if it does, it lands on the GFCI's neutral terminal. Without one, the circuit merely acts as if there is a neutral, but there is no neutral current. Either way, the GFCI's neutral pigtail must land on the panel's neutral bus.cplinc said:Does a 2 pole g.f.c.i. breaker work when there is no neutral ,if so how? we,re installing heat tape on a metal roof and they recommend a g.f.c.i. breaker.
cplinc said:Does a 2 pole g.f.c.i. breaker work when there is no neutral ,if so how? we,re installing heat tape on a metal roof and they recommend a g.f.c.i. breaker.
Doesn't AFCI incorporate 30ma GFP? AFCI breakers must be less than $250.wireman3736 said:Equipment ground fault breakers, I priced one for a homeline a couple of months ago and they quoted me $250.00, crazy
Your right on that, Sometimes my brain has a power outage.wwhitney said:Doesn't AFCI incorporate 30ma GFP? AFCI breakers must be less than $250.
Cheers, Wayne
I don't think so. While it does provide GFP protection, it is not listed for that purpose.Is the AFCI the answer?