I'm 95% certain we just won a job to add a main surge protector on the load side of the ATS and smaller surge protectors at many of the panelboards. The catch is, we can not shut the place down, period. Fortunately, as far as anyone knows, all the critical loads are on rackmounted 20A or larger UPSes.
We also have to shutdown the feed to one of the buildings because it originally had a separate service and is now being fed from a feeder from the main building. We read 14A on the grounding wires in the feeder. The feeder comes out service heads near the original service entrance head and is spliced in the open air with the original conductors. The grounding wires are connected to the RMCs for the original service with pipe bonding clamps. We suspect that the neutral/grounding tie in the original feeder was never broken.
It's gone to be interesting, we're budgeting $5--10K just for temporary power and temporary wiring.
We also have to shutdown the feed to one of the buildings because it originally had a separate service and is now being fed from a feeder from the main building. We read 14A on the grounding wires in the feeder. The feeder comes out service heads near the original service entrance head and is spliced in the open air with the original conductors. The grounding wires are connected to the RMCs for the original service with pipe bonding clamps. We suspect that the neutral/grounding tie in the original feeder was never broken.
It's gone to be interesting, we're budgeting $5--10K just for temporary power and temporary wiring.