240.15(B)(1) question-2008 nec

Status
Not open for further replies.

trekkie76

Member
I have a question regarding this section. According to the Mike Holt Code Change Book, this section is referenced as the reason for handle ties needing to be identified no if's and's or but's.
Yet 240.15(B)(1) says with or without identified handle ties. Is this a misprint, or what am I missing?

Thanks, Gary
 
trekkie76 said:
I have a question regarding this section. According to the Mike Holt Code Change Book, this section is referenced as the reason for handle ties needing to be identified no if's and's or but's.
Yet 240.15(B)(1) says with or without identified handle ties. Is this a misprint, or what am I missing?

Thanks, Gary

All this means is you must use identified handle ties, not a nail through the breaker handles.
 
trekkie76 said:
the without part has thrown me off. It sounds like you can still use the nail :-?

[size=+1]If[/size] you use a handle tie as required by 240.15(B)(1), it has to be identified (See Article 100 for the definition of identified). You don't have to use a handle tie unless required to use one by 210.4(B) if the multiwire branch circuit serves only line to neutral loads.

If you read 210.4(B), it seems to me to require handle ties for a common disconnecting means but not required to be common trip. 210.4(C) Exception 2 requires common trip if you are serving line to line loads with the multiwire branch circuit.

I hope this is not too confusing since the reasoning is a bit circular and it doesn't appear you can ever use a multiwire branch circuit that doesnt have either handle ties or common trip circuit breakers. :confused:
 