Scenario- An existing panel with a conductor exiting the top via conduit to supply wall receptacle outlet, and another conductor ran from bottom of panel within a slab conduit emerging within a second wall to supply another receptacle. Both conductors have been terminated under a single pole 20a breaker. I make reference to 240.20(a) disallowing use because the circuit breaker is not connected in series with each ungrounded conductor. I have always thought the implications for faults, short circuits in individual ocp devices are impaired when the connection has not been made in series, and another path exists at the supply.
Previously mentioned in a (1-4-2k) Question & answer code quandary "The only time two wires can be installed under a single screw or lug is when the terminal is identified for this purpose. Circuit breakers rated not more than 30 ampers are often identified for the termination of two conductors. This can be verified by reviewing the circuit breaker manufacture's catalog".
I would like to keep this separate from 240.21, as I understand tap implications. This "doubling-up" of breaker terminations is a bad practice and blows the tap rule out the window anyway.
What am I missing that would allow double lugging wires under a circuit breaker? What does 240.20(a) really mean?
Thanks for all that you contribute to the industry. I am looking forward to your reply.
Previously mentioned in a (1-4-2k) Question & answer code quandary "The only time two wires can be installed under a single screw or lug is when the terminal is identified for this purpose. Circuit breakers rated not more than 30 ampers are often identified for the termination of two conductors. This can be verified by reviewing the circuit breaker manufacture's catalog".
I would like to keep this separate from 240.21, as I understand tap implications. This "doubling-up" of breaker terminations is a bad practice and blows the tap rule out the window anyway.
What am I missing that would allow double lugging wires under a circuit breaker? What does 240.20(a) really mean?
Thanks for all that you contribute to the industry. I am looking forward to your reply.