Article 240.20 states that Overcurrent Protection Devices are to be located in series with each ungrounded conductor. Is there any article or reason that the overcurrent protection device cannot be located in the neutral or grounded conductor as well. I have a 480v-120v, single phase industrial control transformer that I typically provide overcurrent protect in the ungrounded conductor on the secondary side of the transformer. The customer also wants me to have overcurrent protection in the neutral or grounded conductor on the secondary side as well, basically a double pole breaker, one pole for the ungrounded conductor and one pole for the grounded conductor. I tried to explain to him that it is not necessary and that I thought it wasn't permissable by code, however I am finding out that there is no specific Code article that I can find that actually prohibits overcurrent protection in the grounded or neutral conductor. Thoughts Comments??
Last edited: