Morning everyone
I'm looking at a set of plans, that have #8 copper tapped, line side, to a 60 amp rated disconnect with 30 amp fuses. Looking at the title mentioned code, does this wire need to be #6 to meet the rating of the disconnect, or are 8s sufficient because of the fuses ratings? This is also for a PV installation.
Thanks
I'm looking at a set of plans, that have #8 copper tapped, line side, to a 60 amp rated disconnect with 30 amp fuses. Looking at the title mentioned code, does this wire need to be #6 to meet the rating of the disconnect, or are 8s sufficient because of the fuses ratings? This is also for a PV installation.