240.21(B)(1)

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Reading through the 10 foot tap rule, it doesn’t state the two conductors must terminate in an overcurrent device as does the 25 foot tap rule. This seems odd to me - am I missing something?


Sent from my iPhone using Tapatalk
 

Barney B

Senior Member
Location
Hurst, TX
Occupation
Electrical Instructor/Trainer
Reading through the 10 foot tap rule, it doesn’t state the two conductors must terminate in an overcurrent device as does the 25 foot tap rule. This seems odd to me - am I missing something?


Sent from my iPhone using Tapatalk
The first paragraph of 240.21 requires that tap conductors not supply other conductors except through an OCPD.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Reading through the 10 foot tap rule, it doesn’t state the two conductors must terminate in an overcurrent device as does the 25 foot tap rule. This seems odd to me - am I missing something?


Sent from my iPhone using Tapatalk


I believe all taps must terminate in an overcurrent protective device.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Look at this

b. Not less than the rating of the equipment containing
an overcurrent device(s) supplied by the tap conductors
or not less than the rating of the overcurrent
protective device at the termination of the tap
conductors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The language is that way to permit the use of a fused disconnect as the OCPD for the tap conductor. The tap conductor does not land directly on the OCPD where a fused disconnect is used
 