I am curious whether or not 310.15(B)(7)(2) or (3) applies when sizing a 200 amp feeder and 2-200 amp feeder taps when utilizing the 10' tap rule in a single family dwelling?
10' tap rule. 240.21(B)(1)(1)(a) basically states that the tapped conductors need to be sized no less than the ocpd that the tap conductors land on. So in that case If i had a 200 disconnect. i would need 3/0 Cu which is good for 200 amps at 75 degrees for my feeder tap.
Could be overthinking this but if 310.15(B)(7)(2) applied than you would only need a 4/0 Al or 2/0 Cu for your feeder and feeder taps like you would need for a typical 200 service. Am I on the right track here? Hahah.