Need some help Understanding :
240.21(b)(3)2
Any help Appreciated
Edited in an attempt to break the text lines. Charlie
[ November 06, 2004, 09:19 PM: Message edited by: charlie ]
240.21(b)(3)2
Now I understand the intent, of this, it's the calculation part of it that has me a little confused. Mike holts Understanding the nec gives no example of the calculation, however a stallcup's book I have does. His calculation:The conductors supplied by the secondary of the transformer shall have an ampacity that, when multiplied by the ratio of the secondary to primary voltage, is at least one third the rating of the OCPD protecting the feeder
isn't this calculation showing a primary to secondary ratio, when the code is asking for a secondary to primary ratio?480V/208V *1/3*250A= 192A
This is for a 480-208 step down transformer with a feeder OCPD of 250A
Any help Appreciated