Based on what I can see on this code if you had 3/0 AWG transformer secondary conductor in a separately derived system which terminated to the typical first point of (outside) disconnect and breaker then have the output 3/0 feeder conductor on load side of first disconnect terminate into a buss panel for taps
Then it appears this code would allow a ridiculous 14 AWG conductor to be tapped from this 3/0 feeder without having overcurrent protection on the line side of the 14 AWG conductor for what it would normally require a 15 ampere breaker for small conductors and allow this just because the feeders are located outside
Then the code says you could supply any number of branch circuits with this tap conductor terminating in a breaker with its ampacity.
This doesn’t feel right?
Then it appears this code would allow a ridiculous 14 AWG conductor to be tapped from this 3/0 feeder without having overcurrent protection on the line side of the 14 AWG conductor for what it would normally require a 15 ampere breaker for small conductors and allow this just because the feeders are located outside
Then the code says you could supply any number of branch circuits with this tap conductor terminating in a breaker with its ampacity.
This doesn’t feel right?