Bjenks
Senior Member
- Location
- East Coast of FL
I have an existing commercial client who has a 400A meter outside that feeds underneath the slab up to a 400A main breaker panel. They are now attaching a wing to that building and will require an additional 250A of service. Can I use 240.21(B)(5) to put an 800A fused disconnect outside supplied by 2 sets of 500 kcmil. Then connect the existing feeder of the existing panel (un-bonding the N-G and supplying a G) as a tap to the 800A disconnect. Then run a second tap from the 800A disconnect outside the building to the new wing underneath a new slab to a new 400A main breaker panel? Since both breakers would be 400A I would have to make sure we use a single set of 600 kcmil or 2 sets of 3/0.
It seems that I can run all types of unlimited length taps from the fused disconnect as long as I stay outside of the building and I feed into a breaker that is size greater than or equal to the rating of the cable.
It seems that I can run all types of unlimited length taps from the fused disconnect as long as I stay outside of the building and I feed into a breaker that is size greater than or equal to the rating of the cable.