jclint07
Member
- Location
- south missouri
As I read this code section, for tap conductors under 25' to be considered/ used as tap conductors then all 3 conditions have to comply. But doesn't condition #1 contradict condition #2?
Condition #1- tap conductors ampacity is not less than 1/3 the rating of the overcurrent protection device.
(So then overcurrent protection device is allowed to be OVERSIZED for the conductor ampacity?)
Condition #2- tap conductors terminate in a circuit breaker or set of fuses that LIMIT the load to the ampacity of the tap conductors.
(So then overcurrent protection device must be sized FOR conductor ampacity?)
This NEC 2008 code section is confusing to me. Any help would be greatly appreciated.
Condition #1- tap conductors ampacity is not less than 1/3 the rating of the overcurrent protection device.
(So then overcurrent protection device is allowed to be OVERSIZED for the conductor ampacity?)
Condition #2- tap conductors terminate in a circuit breaker or set of fuses that LIMIT the load to the ampacity of the tap conductors.
(So then overcurrent protection device must be sized FOR conductor ampacity?)
This NEC 2008 code section is confusing to me. Any help would be greatly appreciated.