Does 240.21(C )(4) still apply if the transformer is located inside the building but the secondary conductors are routed outside to the load?
The '17 Code added a bit of wording to clarify the for (C)(4) to apply the conductors must be outside the building except at the point of load termination.
Depending on your transformer manufacturer and size, that often simply involves adding some rain shields