(NOTE: I see that there are two current threads discussing issues similar to mine. But I think my question is different enough to give it its own thread.)
I am involved in the design of a new laboratory facility (presently a dirt field). Two medium voltage switches will serve two transformers (12.47kv to 480/277V, 3000 KVA each). They in turn will feed a ?Main-Tie-Main? switchboard that is located perhaps 150 feet away. The MV switches, the transformers, and the switchboard will all be within the same building, at grade level. We are early enough in the design process that I can call for conduit runs under the slab.
Question: If I run the secondary conductors from the transformers to the switchgear below the slab, can I treat these conductors as being ?outside secondary conductors??
I would like to take advantage of 240.21(C)(4), and not install an overcurrent device at the transformers. But these conductors will be "within the building" from their point of connection to the transformers until they reach the underground duct bank below the transformers. Does that fact cause a problem with my plan?
I know that 230.6 states that conductors can be considered ?outside the building? in the type of installation I am contemplating. But that is not a ?definition,? being outside Article 100, and I don?t know if it would apply to Article 240. Also, in 230 it is presumed that the conductors begin their run from a point outside the building, and never become "within the building" until they are stubbed up from below.
FWIW, the 2004 California Electrical Code applies, and it is based on the 2002 NEC. But I don?t see anything significantly different between this and the 2005 NEC.
I am involved in the design of a new laboratory facility (presently a dirt field). Two medium voltage switches will serve two transformers (12.47kv to 480/277V, 3000 KVA each). They in turn will feed a ?Main-Tie-Main? switchboard that is located perhaps 150 feet away. The MV switches, the transformers, and the switchboard will all be within the same building, at grade level. We are early enough in the design process that I can call for conduit runs under the slab.
Question: If I run the secondary conductors from the transformers to the switchgear below the slab, can I treat these conductors as being ?outside secondary conductors??
I would like to take advantage of 240.21(C)(4), and not install an overcurrent device at the transformers. But these conductors will be "within the building" from their point of connection to the transformers until they reach the underground duct bank below the transformers. Does that fact cause a problem with my plan?
I know that 230.6 states that conductors can be considered ?outside the building? in the type of installation I am contemplating. But that is not a ?definition,? being outside Article 100, and I don?t know if it would apply to Article 240. Also, in 230 it is presumed that the conductors begin their run from a point outside the building, and never become "within the building" until they are stubbed up from below.
FWIW, the 2004 California Electrical Code applies, and it is based on the 2002 NEC. But I don?t see anything significantly different between this and the 2005 NEC.