Dale001289
Senior Member
- Location
- Georgia
Is there any reason to add 25% to transformer secondary conductors? For example the engineer is saying if the MCB is rated 1200A in the SWGR, you need the secondary conductors to be rated 1200A x 1.25% = 1500A. But I see no evidence of that in 240.21(C)(4)
Sent from my iPhone using Tapatalk