Re: 240.21(c)(6)
When ever someone has called me with regard to a 75kva,75kva, 480-208y/120 transformer and has a problem nuisance tripping the first thing I ask is why the 100a breaker? The answer usually is that it is the largest breaker that can be installed in the panel which is a 1" per pole panel. It was never a consideration that there would be a need for a breaker greater than 100a, that 100a was enough.
I've had more application issues because of that 100a breaker limitation.
Without the 25' tap rule you are allowed to go to a 125a rated breaker which they can't even do unless their panel allows the installations of a 150a frame breaker which in most cases they can not.
20/20 hind sight would now be that the panel should have been ordered with a subfeed breaker dedicated to feed the transformer or a panel with provisions for up to a 250a frame for a 225a rated breaker while applying that 25' tap rule.
Incidentally, regarding the 25', am I to understand that the 25' can be a measurement taken from the pri. OCPD to the sec. OCPD and not be limited to the distance to the transformer?
What is you interpretation?