The "ratio" wording always confuses me.
If I have a 75 kva 480 to 208/120 transformer protected by a primary 100 amp breaker, what is my minimum size secondary conductor ?
On right track, but wrong way with the ratio - that would be correct if stepping up instead of down with the transformer. If primary has a 100 amp OCPD, then the secondary current is 230 amps (before it gets into trip range of the 100 amp primary device) and 1/3 of that is 76.7.My thinking (probably wrong) would be that you need a conductor with an ampacity of 1/3 of OCP X the ratio (480:208 or ,43) or a 15 amp conductor, (100 X 1/3 X .43)
I do believe Kwired calculation is correct.
X2....