Chrispacc
Member
- Location
- Sunrise FL
I NEED help!!!! I Have a 480V panel feeding a 75KVA X-FMR on the primary side, on the secondary side I have an 80' run on 4/0THHN to a 225AMP MCB panel where it HAS overcurrent protection!!! This inspector is calling me out saying that I cannot go over 25' without a disconnect? I am insisting that that is just a TAP rule.... there is a difference between a tap rule and secondary feeders. check out the definition of TAPS in 240.2....let me know ASAP!