240.21 (C) (4) Outside Secondary Conductors.
(2) The conductors terminate at a single circuit breaker or a single set of fuses that limit the load to the ampacity of the conductors. This single overcurrent device shall be permitted to supply any number of additional overcurrent devices on its load side.
Am I understanding this correctly. That multiple taps to multiple disconnects direct from the transformer secondary are not permitted? Only permitted after a first disconnect.
(2) The conductors terminate at a single circuit breaker or a single set of fuses that limit the load to the ampacity of the conductors. This single overcurrent device shall be permitted to supply any number of additional overcurrent devices on its load side.
Am I understanding this correctly. That multiple taps to multiple disconnects direct from the transformer secondary are not permitted? Only permitted after a first disconnect.