Construction has a 100A CB in a panelboard feeding 2, 480V welding receptacles - each WR has a 60A fuse.
They’re using #1AWG from the CB, then tapping in a box that’s approx 20’ above the floor in a high bay manufacturing bldg with #6’s and running to each welding receptacle approximately 80’ away from the tapped point.
This fits 240.21(4) except the height isn’t 30’ above the floor. Is this a Code acceptable?
Thanks


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Since you are supplying welders, 630.12 will come into account and it appears 630.12(B) will allow that install.
 