I need some help on 240.21(b)1 or (b)2 ?
Working on a remodel of a local restaurant. Plans call for a new 225 lighting panel. MDP at 6 throws already.
So Installed a new 600 main breaker feeding parallel 350s. to the trough
where i taped with 3 awg to 3 new nema 1 dead fronts.
In the dead fronts i used the salvaged (225) (175) and new (225) feeder breakers. fist 2 no problem nippled to the trough
With space very tight i needed to install the last dead front aprox. 14 feet (wire length ) away for the feeder tap
Question is does this last tap comply with 240.21 b 2 ?
Working on a remodel of a local restaurant. Plans call for a new 225 lighting panel. MDP at 6 throws already.
So Installed a new 600 main breaker feeding parallel 350s. to the trough
where i taped with 3 awg to 3 new nema 1 dead fronts.
In the dead fronts i used the salvaged (225) (175) and new (225) feeder breakers. fist 2 no problem nippled to the trough
With space very tight i needed to install the last dead front aprox. 14 feet (wire length ) away for the feeder tap
Question is does this last tap comply with 240.21 b 2 ?