I think I have only ever done 3 taps in my 15 years of being in the field. Attached is the set up I have. I can't get a 200 amp MB Panel with feedthrough lugs. So I have to install a little panel on back side, because owners wants outlets and 240 outlet next to Meter.
Attached are my 200 Disconnect I will be using. https://www.platt.com/platt-electri...Type/Eaton/ECCVH200R/product.aspx?zpid=164978
They are tight fitting and hate splicing in them because of that.
The load I need is only 40 amps. If I splice after one of the 200 amps then I can get by with 10kaic breakers ( I believe ? still looking into Series rating for breakers ) after that so I can use small little panel with breaker and hold down kit.
400 amp Meter enclosure
www.platt.com
If I tap in the load side of the meter than technically the Panel I will feed will now have to have 25kaic breaker feeding it. Little more expensive but I have a lot of room to tap in the 400 amp meter enclosure.
In ground transformer is next to equipment and AIC is 15900
Thank you
Attached are my 200 Disconnect I will be using. https://www.platt.com/platt-electri...Type/Eaton/ECCVH200R/product.aspx?zpid=164978
They are tight fitting and hate splicing in them because of that.
The load I need is only 40 amps. If I splice after one of the 200 amps then I can get by with 10kaic breakers ( I believe ? still looking into Series rating for breakers ) after that so I can use small little panel with breaker and hold down kit.
400 amp Meter enclosure
Eaton B-Line 324 N :: 400A, 4P, 4 Jaw, Ring-Type Meter Socket :: PLATT ELECTRIC SUPPLY
400 Amp, 1-Phase, 4 Jaw, Ring-Type. 3-Wire, 600V, Surface Mount, Overhead/Underground Feed. Manual Circuit Closing Bypass, NEMA 3R. HxWxD: 32" x 14" x 6". Line and Load lug wire (1) 4awg to 600mcm or (2) 1/0awg to 250mcm *** Item is in Manufacturer Allocation. Quantity is Subject to Approval...
In ground transformer is next to equipment and AIC is 15900
Thank you