240.24(E) interpretation (2017 NEC)

Status
Not open for further replies.

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
240.24(E) states that regarding overcurrent protection shall not be located in a bathroom, other than supplemental overcurrent protection. Never noticed that added exception. Does that allow for a "subpanel" to be in the bathroom? Or what would an example of a supplemental overcurrent protection be?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
240.24(E) states that regarding overcurrent protection shall not be located in a bathroom, other than supplemental overcurrent protection. Never noticed that added exception. Does that allow for a "subpanel" to be in the bathroom? Or what would an example of a supplemental overcurrent protection be?
Ul 1077 covers supplementary protectors. Usually used to protect a specific device as opposed to a circuit. So it could be something built in to a device.
 

retirede

Senior Member
Location
Illinois
IMO, the breakers in a subpanel are primary OCP for branch circuits originating there and cannot be considered supplementary.

An example of supplementary would be a fuse commonly located at a gas furnace disconnect switch. The branch circuit is already protected at its ampacity, so the fuse is supplementary.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Thanks, had someone argue that they could put a subpanel in the bathroom trying to use that section and I've never noticed that little piece. I didn't think that would be allowed but couldn't think of an example of what IS a "supplemental overcurrent protection".
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks, had someone argue that they could put a subpanel in the bathroom trying to use that section and I've never noticed that little piece. I didn't think that would be allowed but couldn't think of an example of what IS a "supplemental overcurrent protection".
I agree. That would be a stretch.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The most common supplemental overcurrent protection that I have come across is the fuses sometimes specified in luminaires with ballasts to keep the branch circuit OCPD from opening when the ballast fails.

Note that where the code requires OCPD, it must be suitable for use as "branch circuit overcurrent protection". OCPDs that are marked "supplemental overcurrent protection" are not permitted to provide the protection that the code requires for branch circuits.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
240.24(E) states that regarding overcurrent protection shall not be located in a bathroom, other than supplemental overcurrent protection. Never noticed that added exception. Does that allow for a "subpanel" to be in the bathroom? Or what would an example of a supplemental overcurrent protection be?

If you are in a building other than those mentioned, ie a commercial area bathroom, then you can have a sub panel in the bathroom. The nec does not allow service equipment in the bathrooms of these other places.
 