An overcurrent coordination study identified NEC 240.4 violations in circuits from switchboard breakers to VFDs and starters on a project I'm reviewing. The installation meets requirements of Article 430 so believe it complies with 240.4(G). The part that's a little concerning to me is that motor branch circuits are required to have overload and short circuit protection per 430.31 and 430.51, but feeder circuits are only required to have short circuit protection (430.61). Do feeders serving motor loads need both overload and short circuit protection to meet the overcurrent protection requirements of 240.4?
Two examples:
200A breaker - #2/0 CU conductors - Motor Starter - #2/0 CU conductors - 124FLA motor.
400A breaker - #350 CU conductors - VFD (240A input rating) - #350 CU conductors - 240FLA motor.
Does anyone see a violation of 240.4 here?
Thanks
An overcurrent coordination study identified NEC 240.4 violations in circuits from switchboard breakers to VFDs and starters on a project I'm reviewing. The installation meets requirements of Article 430 so believe it complies with 240.4(G). The part that's a little concerning to me is that motor branch circuits are required to have overload and short circuit protection per 430.31 and 430.51, but feeder circuits are only required to have short circuit protection (430.61). Do feeders serving motor loads need both overload and short circuit protection to meet the overcurrent protection requirements of 240.4?
Two examples:
200A breaker - #2/0 CU conductors - Motor Starter - #2/0 CU conductors - 124FLA motor.
400A breaker - #350 CU conductors - VFD (240A input rating) - #350 CU conductors - 240FLA motor.
Does anyone see a violation of 240.4 here?