I am having a hard time understanding this.
240.4 (B) permits the use of the next larger standard overcurrent device. Does this mean that 240.4(B) permits no overload protection for device rated 800A or less?
For example, 500kcmil cu conductor has an allowable ampacit of 380A. Per 240.4(B), this conductors can be protected by a 400A overcurrent protective device. But what if, some reason, this conductor is overloaded to 390A, then this conductor is not going to be protected by 400A cb. Correct?
That said, my questions are
1) why does the code permit the next larger standard overcurrent device?
2) Why not go with the next smaller overcurrent devices?
3) Why this is only permitted to devices with 800A or less?
4) Why not with devices with 800A or more?
Another fact that I am having hard time understanding is the rating of the circuit breaker. Most of circuit breakers are rated 80% of its rating, expect the ones with 100% reated ones. 400A MCCB is only rated 320A.
So go back to our example, a 400A circuit breaker is protecting a 500Kcmil condutor (380A). But if your loads exceed 320A, your 400A circuit breaker is not going to provide overcurrent protection anymore because it exeeds its rating. What am I missing here? Please help.
240.4 (B) permits the use of the next larger standard overcurrent device. Does this mean that 240.4(B) permits no overload protection for device rated 800A or less?
For example, 500kcmil cu conductor has an allowable ampacit of 380A. Per 240.4(B), this conductors can be protected by a 400A overcurrent protective device. But what if, some reason, this conductor is overloaded to 390A, then this conductor is not going to be protected by 400A cb. Correct?
That said, my questions are
1) why does the code permit the next larger standard overcurrent device?
2) Why not go with the next smaller overcurrent devices?
3) Why this is only permitted to devices with 800A or less?
4) Why not with devices with 800A or more?
Another fact that I am having hard time understanding is the rating of the circuit breaker. Most of circuit breakers are rated 80% of its rating, expect the ones with 100% reated ones. 400A MCCB is only rated 320A.
So go back to our example, a 400A circuit breaker is protecting a 500Kcmil condutor (380A). But if your loads exceed 320A, your 400A circuit breaker is not going to provide overcurrent protection anymore because it exeeds its rating. What am I missing here? Please help.