dummycheck
Member
- Location
- Texas
- Occupation
- Engineer
I'm working on a project where I'm going to be serving a 800A service entrance with a new transformer. I was planning on using (2) sets of 500kcmil that would get me to 760A (actual load will be less than 760A), use 240.4(B) to round-up to 800A OCPD and call it a day. But as I was looking through the tap rules I noticed that 240.21(C) specifically states that transformer secondary conductors shall not be permitted to use 240.4(B).
I'm sure the intention is for step-down transformers, but does this also apply to service transformers and service entrance conductors? I know for a fact that I've seen 800A service entrances with (2) sets of 500kcmil in existing installs.
What is the thought behind not allowing the 240.4(B) on the transformer secondary?
I'm sure the intention is for step-down transformers, but does this also apply to service transformers and service entrance conductors? I know for a fact that I've seen 800A service entrances with (2) sets of 500kcmil in existing installs.
What is the thought behind not allowing the 240.4(B) on the transformer secondary?