Can the supplementary protection in 240.5(A) be upstream of a flexible cord? (standard appliance or lighting fixture cord)
Is that what 210.19(4) Exeption 2 is saying?

I am looking at T400.5 (A) column B For 2 CC standard Thermoplastic cord sets.
13A for 16AWG and 18A for 14 AWG.

240.4(B) can not be used for sizing flexable cords in relation to 240.5(A) agreed?
240.4 opens with "other than flexible cords".

Thanks in advance!
 